Available nowNewcastle, Lake Macquarie & the Hunter · Urgent calls 4am–9:30pm, 7 days

Urgent? Call Lachie now

Breaker trips the moment you reset it? That's a short, stop resetting and call us

A breaker that trips instantly is reacting to a short circuit. Each reset sends a burst of current into it. Leave it off. Lachie finds and repairs it.

5.0 from 24 Google reviewsUpfront pricesLicensed & insured

Meter box with a smart meter, a main switch and a new row of labelled safety switches, on an older black backing board with an asbestos warning sticker

Offers on this job

  • $0Call-out feeOn booked jobs, Monday to Friday, 7am to 5pm.
  • $60 offYour first jobNew customers save on their first booked job.

The $0 call-out is for booked jobs: a time we have set together, with the work going ahead. It applies Monday to Friday, 7am to 5pm. After-hours emergency call-outs have a minimum charge of $349 + GST, and Lachie confirms it on the phone before he drives out.

Where a short circuit hides

A short is live touching neutral or earth with almost nothing in between. The breaker cuts it the instant power reaches it, so it snaps straight back off.

Where the short circuit can be when a breaker trips straight awayA switchboard with one circuit breaker tripped and an arrow showing it snapping back down. Its dead circuit runs through the wall past a nail through the cable that is sparking, to a burnt power point and to a heater plugged in and sparking at its cord. The main switch is at the top left of the board. Switchboard In the wall 12345
What the numbers show
  1. The breaker that snaps back
  2. A nail or screw through a cable
  3. A burnt power point or switch
  4. A faulty appliance still plugged in
  5. The main switch
What you're looking at: Your switchboard is on the left, with a breaker that snaps straight back off when you push it up (the arrow). Its circuit runs through the wall to the usual causes of a short: a nail through a cable, a burnt power point and a faulty heater still plugged in.Simplified drawing. Red shows the fault or a switch that has tripped. Every property is different: Lachie will show you what's going on at yours.
  1. The breaker that snaps back

    It drops the instant you push it up, often with a snap. That's the fast trip for a short, not an overload. Unplug things on that circuit, try once more, then leave it off.

  2. A nail or screw through a cable

    A picture hook, shelf or renovation can drive a fastener through a cable in the wall. It may trip at once or weeks later. Leave it in place and don't pull it out.

  3. A burnt power point or switch

    A loose connection heats up until the insulation melts and the wires touch. Brown marks, a warm plate or buzzing beforehand are the warning signs.

  4. A faulty appliance still plugged in

    A burnt-out element, a failed motor or a crushed cord. If the breaker holds once that appliance is unplugged, it's the one. Don't use it until it's checked.

  5. The main switch

    A big enough short can trip the main switch as well, and the whole house goes dark. If it won't hold, leave it off. Don't keep resetting it.

What usually causes a short: more detail on each cause

A short is live touching neutral or earth with almost nothing in between. A huge current flows, and the breaker cuts it in a fraction of a second. These are the usual places it happens.

  • A faulty appliance or cord Most common

    A burnt-out element, a failed motor, or a cord crushed under furniture or chewed by a pet. If the breaker holds once that appliance is unplugged, it is the one.

  • A nail, screw or drill through a cable

    Picture hooks, shelves, new kitchens and plaster repairs. The fastener bridges the wires inside the cable. It may trip right away, or weeks later as things settle.

  • A burnt power point or switch

    A loose connection overheats until the insulation melts and the wires touch. You may have noticed brown marks, a warm plate or a buzzing sound beforehand.

  • A failed light fitting or fan

    Old downlight transformers, LED drivers and fittings that have cooked in the ceiling can short out. Ceiling fans and exhaust fans on the lighting circuit can too.

  • Water in a fitting

    A lot of water in an outdoor power point, a light under a roof leak or a flooded junction box can short the circuit, not just leak to earth.

  • Rodent damage in the roof Older homes

    Rats and possums chew through cable insulation in the roof. Once two bare wires touch, it's a dead short. It's often near a junction box or where cables cross the timber.

Signs it's a short, not an overload

An overload takes time to trip a breaker. A short trips it the instant power reaches it. That difference tells you a lot.

  • It drops the instant you push it up

    No delay at all, often with a loud snap. That's the breaker's fast trip, which reacts to a short circuit, not to load.

  • It trips with everything unplugged

    Then the short is in the fixed wiring, a light fitting, a power point or a hardwired appliance like the oven, not in something plugged in.

  • It stays on once one thing is unplugged

    Then the short is most likely inside that appliance or its cord. Leave it unplugged and have it checked before anyone uses it again.

  • There was a bang, flash or smell

    A short can flash and bang where it happens, and leave a burning smell or black marks on a power point, switch or plug. Note where it was.

  • Something was just drilled, nailed or screwed

    A picture hook, a new shelf or a renovation. A fastener through a cable is a classic cause. Leave it in place and don't pull it out.

  • A light blew as it tripped

    An old-style globe can arc as it blows and trip the lighting breaker. If the breaker then holds with that light switched off, the globe was likely the cause.

How we find and repair a short

We make it safe, find the exact spot, then repair it properly. No guessing and no repeated resets.

  1. 1

    Make it safe on the phone

    Lachie asks what happened when it tripped, and whether there was a bang, flash or smell. If it sounds like a fire risk, he'll tell you what to switch off and whether to call 000 first.

  2. 2

    Test the circuit with the power off

    At the board, he isolates the circuit and tests between live, neutral and earth with the power off. A short shows up clearly, without risking another trip.

  3. 3

    Pin down the spot

    He separates the circuit at power points, lights and junction boxes and tests each section until the short is found. Burn marks, melted insulation or a nail through the cable usually show where it is.

  4. 4

    Repair, test and switch on

    The damaged cable, power point, fitting or connection is replaced, the whole circuit tested, and the breaker switched on to stay on. You get a Certificate of Compliance for Electrical Work (CCEW) where the work needs one.

Repair the spot, replace the cable, or deal with the appliance: your options side by side

The fix depends on where the short is and how much damage the heat has done.

Repair at the point of the short

A single burnt power point, a failed fitting or one damaged joint

  • Quick, often on the same visit, with the circuit back on that day.
  • If heat has damaged the cable further along, a spot repair isn't enough. We check before we close up.
  • For good, once the damaged part is replaced.

Replace the damaged section of cable

A nail or screw through a cable, or rodent damage in the roof

  • New cable where the old one was hit, usually run through the roof or under the floor.
  • May mean a small hole in a wall or ceiling to reach it. We tell you where first.
  • Decades.

Repair or replace the appliance

A short inside an appliance or its cord

  • The circuit is fine, so the power is back on as soon as the appliance is unplugged.
  • Plug-in appliances usually go back to the maker's service agent, or get replaced.
  • Depends on the appliance.

A short circuit can melt cable and start a fire inside a wall. The breaker stops that every time it trips. Don't reset it again until the short has been found.

What you can safely do now

Stop resetting. These are the only things to do until we arrive.

Safe to do now

  • Leave the breaker off.
  • Unplug everything on that circuit, if it's dry and safe to touch.
  • If you reset it before unplugging anything, you can try it once more with everything unplugged. If it trips again, stop there.
  • Note what happened: a bang, a flash, a smell, or something just switched on or drilled.
  • Take a photo of the switchboard, and of any marks on a power point or plug, from a safe distance.

Don't

  • Don't keep resetting it. Each try sends a burst of fault current into the short.
  • Don't hold it on, tape it up or have it swapped for a bigger breaker.
  • Don't pull out a nail or screw you think has hit a cable. It may be live.
  • Don't open power points, lights or the switchboard to look for it.

Call straight away if

  • There was a bang, flash or burning smell, or there are scorch marks anywhere. Switch off the main switch if it's safe to reach. If there's smoke or fire, get everyone out and call 000. Never put water on it.
  • It trips with everything on that circuit unplugged.
  • The fridge, freezer, lights or medical equipment are on that circuit.
  • You feel a tingle or shock from a tap, the shower or an appliance. Keep everyone away and call Ausgrid on 13 13 88 first.
Call Lachie

What locals say

5.0 from 24 Google reviewsWord for word, nothing edited.

  • We have had Lachie from Cazlec do a lot of work on our home in Merewether. He has always been honest and reliable and we know he will enjoy many years of success.

    todd blatchford, Merewether Google review

  • I've used Lachie @ Cazlec on several occasions now and highly recommend. He does a great job, is reliable, on time, and always leaves everything clean and tidy. Pricing is very fair as well.

    Doug Norton Google review

  • We have the pleasure of working with Lachie and his team at Clarke & Co Property Management for both emergency call-outs and general maintenance work. Lachie is always quick to respond, professional, and happy to help whenever needed. His communication and workmanship are consistently excellent.

    Calais Horrigan Google review

  • Cazlec (Lachlan) did a thorough and tidy job for a very reasonable price. Prompt and professional, I'll happily refer him to others. Thanks!

    Samuel Roberts Google review

  • We've been using Cazlec Electrical for our business and have always been impressed with the quality of service. They arrive when they say they will, and take the time to explain any issues and solutions clearly.

    Bobby Google review

  • Lachlan and his team have been extremely prompt when we have needed an electrician. They are professional and personable and would highly recommend them. No job too small.

    Marie Smith Google review

  • We have used Cazlec Electrical on a number of occasions and have always had a quick response and have been extremely pleased with the work they have done. I would highly recommend this company.

    Terence Coombes Google review

  • I have been using Cazlec Electrical for the last 3 years. Always on time. No hassle and gets the job done. Highly recommend.

    steven thomas Google review

  • Professional and outstanding tradesmen.

    Rob Iacopetta Google review

  • Highly recommend. Great service!

    Sharyn Rogers Google review

More reviews

Questions people ask

Why does my breaker trip as soon as I reset it?

Because there's a short circuit on that circuit right now. Live is touching neutral or earth, in an appliance, a power point, a fitting or a damaged cable. The breaker's fast trip reacts in a fraction of a second. Leave it off and call.

Is a short circuit dangerous?

Yes. A short draws a huge burst of current, which can melt cable and start a fire in a wall. The breaker is what stops that. Every reset is another burst, so stop trying it and get the short found.

How do I know if it's an appliance or the wiring?

Unplug everything on that circuit and try the breaker once more. If it holds, an appliance is the likely cause, so leave it unplugged. If it still trips instantly, the short is in the wiring, a fitting or something hardwired.

Can the breaker itself be faulty?

Rarely. A worn breaker usually trips too easily under load, not instantly with nothing on. We test the circuit before blaming the breaker, because a new breaker won't fix a short.

Breaker tripped after drilling into the wall?

The nail, screw or drill bit has most likely hit a cable. Leave it where it is, don't pull it out, and leave the breaker off. We'll find the damaged section and replace it, usually with only a small hole to patch.

Can you come now?

Yes. Lachie takes urgent calls from 4am to 9:30pm, 7 days across Newcastle & Lake Macquarie, and works Monday to Friday, 7am to 5pm. Call 0402 079 953, tell us what happened, and leave the breaker off while you wait.

Lachie

Get a free quote from Lachie

Four quick details and Lachie will be in touch. Your quote is back within 24 hours, with no hidden fees.

  • Free quotes. Back to you within 24 hours, in plain English, with no hidden fees.
  • Upfront pricing. You know the cost before any work starts.
  • 100% satisfaction guarantee. Not happy with the work? Lachie comes back and makes it right, free.
  • Quality guarantee. Every job done to the Australian wiring rules (AS/NZS 3000), with parts that meet Australian standards, and tested before we leave.

Rather talk it through? Call Lachie on 0402 079 953

We use your details only to quote and book this job. Privacy.